CottageFarm wrote:What amperage is the circuit breaker in your service panel?
60 in the panel and the unit. Unit breaker is what trips.
CottageFarm wrote:What amperage is the circuit breaker in your service panel?
greybeard wrote:If anything, I would think the lack of a somewhat restrictive duct would cause it to pull fewer amps..not more.
I assume it's rated 240 volts due to the heater strips. 60A should be plenty good.
CottageFarm wrote:There are, unfortunately, several things that could be at fault. Need to eliminate one at a time.
1.Inspect all wiring carefully. Especially hot wires. Look for any nicks or anything that could be grounding out.
Verify all connections are tight and free of corrosion.
2.You didn't mention whether the fan comes on? I don't want to assume anything...
3.Try connecting a thermostat instead of the switch.
4.Its not common, but breakers do go bad, especially if they've been tripped many times.
5.Next step is testing or replacing parts. I would start with the transformer, limit switches, and contactors/sequencers in that order.
Lots of good videos on youtube to walk you thru different diagnostic tests for different parts.
The upside is this is likely an inexpensive, but frustrating process.
CottageFarm wrote:The solution should cost substantially less than buying 2 5k units
Do we know why the unit was originally replaced? Just looking for potential starting points....
Any chance you have a clamp style multi-meter to test the voltage running thru wires both upstream and downstream of the circuit breaker on the unit?
If not....If it were mine, I think the first thing I would test is the circuit breaker in the unit. Either swap it with another one or bypass it to see if it trips the breaker in the panel.
ddd75 wrote:what size wiring are you using to connect it? should be a 6
you can bypass the systems breakers and direct wire it. That will eliminate the furnace breaker if the main 60 trips as well.
tom4018 wrote:ddd75 wrote:what size wiring are you using to connect it? should be a 6
you can bypass the systems breakers and direct wire it. That will eliminate the furnace breaker if the main 60 trips as well.
It is #6 wire. It runs a couple minutes before tripping. I would think if I had something wired wrong it would instantly trip.
tom4018 wrote:I think I found the problem. Wires on unit side of breaker were loose, guess they loosened them for some reason on take out. Heating elements are pulling about 21 amps each and 45 for the whole unit. Does that seem normal?
tom4018 wrote:I think I found the problem. Wires on unit side of breaker were loose, guess they loosened them for some reason on take out. Heating elements are pulling about 21 amps each and 45 for the whole unit. Does that seem normal?